Originally posted by gellfex
View Post
(B) Not Permitted for Use as Grounding Electrodes.
The following systems and materials shall not be used as
grounding electrodes:
(1) Metal underground gas piping systems
There IS a requirement IF the gas piping is likely to become energized, that it be "bonded to" a legitimate grounding electrode. That is a slight but important difference from being THE actual PE, and seems to allow bonding the internal piping, with no requirement for pipes outside.
(B) Other Metal Piping. If installed in, or attached to, a
building or structure, a metal piping system(s), including
gas piping, that is likely to become energized shall be
bonded to any· of the following:
(1) Equipment grounding conductor for the circuit that is
likely to energize the piping system
(2) Serviceequipinent enclosure
(3) Grounded conductor at the service
(4) Grounding electrode conductor, if of sufficient size
(5) One or more grounding electrodes used
Comment