  • #31
    Steam pressure gauges are always mounted on top of the boiler, never in the water. Link to a proper Steam Table chart. Steam-Tables.pdf (byworth.co.uk) Yes I have actually worked on steam boilers and remember the gauge reads in PSI not Absolute. Water in column 1 ft high and 1 inch in diameter weighs .433 lb.
    Last edited by wmgeorge; 01-16-2022, 03:05 PM.
    Retired - Journeyman Refrigeration Pipefitter - Master Electrician

    Comment


    • #32
      Originally posted by wmgeorge View Post
      Steam pressure gauges are always mounted on top of the boiler, never in the water. Link to a proper Steam Table chart. Steam-Tables.pdf (byworth.co.uk)
      Like I said, some people can intuit these things, others can't. A dial gauge is not a tube manometer. It's a stupidly simple idea, if the pressure outside the vessel is lower than inside, the water will rise in the tube above the level in the vessel. Just does. Exactly how a 'swan' barometer works, when atmospheric pressure drops, the water goes up the tube. But if you held a candle under there, it would also go up as the water and trapped air expanded.

      Click image for larger version

Name:	il_794xN.2125555102_6tha.jpg
Views:	211
Size:	117.1 KB
ID:	1981082
      Location: Jersey City NJ USA

      Comment


      • #33
        Since your an expert, its going to be interesting how you solve this problem.
        Retired - Journeyman Refrigeration Pipefitter - Master Electrician

        Comment


        • #34
          Originally posted by gellfex View Post

          Like I said, some people can intuit these things, others can't. A dial gauge is not a tube manometer. It's a stupidly simple idea, if the pressure outside the vessel is lower than inside, the water will rise in the tube above the level in the vessel. Just does. Exactly how a 'swan' barometer works, when atmospheric pressure drops, the water goes up the tube. But if you held a candle under there, it would also go up as the water and trapped air expanded.

          Click image for larger version

Name:	il_794xN.2125555102_6tha.jpg
Views:	211
Size:	117.1 KB
ID:	1981082
          Laws of physics are not subject to intuition. If you want to measure the steam pressure inside a boiler, you have to connect a pressure gauge above the water level to be precise in your measurements.

          I am not familiar with steam boiler design and do not want to make any comments on how the pressure is measured. But pressure at the bottom of the boiler is higher than the steam pressure. This is due to the weight of water - exactly as wmgeorge said. Try to tell a deep water diver that depth has no affect on pressure. For your information 1 psi = 2.3067 ft of water at 32 deg. F, so the water depth has quite significant affect on pressure.

          Comment


          • #35
            So if a farmer had a 12 foot high round tank that was sealed completely and put in exactly 10 ft of water, and installed a pressure gauge at the top and bottom.... and added one psi of air pressure at the top of the said tank, what would the gauge at the bottom measure in psi gauge read?
            Retired - Journeyman Refrigeration Pipefitter - Master Electrician

            Comment


            • #36
              Originally posted by wmgeorge View Post
              So if a farmer had a 12 foot high round tank that was sealed completely and put in exactly 10 ft of water, and installed a pressure gauge at the top and bottom.... and added one psi of air pressure at the top of the said tank, what would the gauge at the bottom measure in psi gauge read?
              5.3 psi.

              Comment


              • #37
                Originally posted by wmgeorge View Post
                So if a farmer had a 12 foot high round tank that was sealed completely and put in exactly 10 ft of water, and installed a pressure gauge at the top and bottom.... and added one psi of air pressure at the top of the said tank, what would the gauge at the bottom measure in psi gauge read?
                Different kind of gauge, different reading.

                The gauge at the bottom is reading inside pressure vs outside pressure. It does not cancel out the water pressure so it reads air pressure PLUS "depth pressure".

                The water manometer would just fill with water until it was in balance, with the pipe and the boiler both registering the same height. Now that the "depth pressure" is balanced (canceled) out, the DIFFERENCE between water levels is the "extra" pressure of steam in the system (if any), or in the farmer's tank, the one lb air pressure.
                CNC machines only go through the motions.

                Ideas expressed may be mine, or from anyone else in the universe.
                Not responsible for clerical errors. Or those made by lay people either.
                Number formats and units may be chosen at random depending on what day it is.
                I reserve the right to use a number system with any integer base without prior notice.
                Generalizations are understood to be "often" true, but not true in every case.

                Comment


                • #38
                  Originally posted by mikey553 View Post

                  5.3 psi.
                  Correct!! I wish I had a prize!! A pressure gauge is a pressure gauge! No one uses a manometer on a boiler except on measuring gas pressure.
                  Last edited by wmgeorge; 01-16-2022, 04:43 PM.
                  Retired - Journeyman Refrigeration Pipefitter - Master Electrician

                  Comment


                  • #39
                    Originally posted by wmgeorge View Post

                    ...............A pressure gauge is a pressure gauge! .....................
                    Not really...... There are many kinds of pressure gauge. Some register pressure above atmospheric. A few measure absolute pressure (vs a vacuum). And a manometer reads DIFFERENTIAL pressure. The DIFFERENCE of pressure at one end vs the other.

                    Your pressure gauge ....... the one you wanted to out on the tank. What does it read when it is just sitting on the table?

                    What would it read if you just tossed it into that tank of water and it sank to the bottom?............................. yep, same thing it read on the table. Zero.

                    Why is that?

                    Same exact reason why the manometer will read perfectly correctly on the tank of water.

                    And, speaking of that tank of water...... you seem to be saying that if the manometer was 15 feet tall, and was filled with water to the same height as the tank, that if a tube is run from one side of it to the top of the tank, that it would read WRONG.

                    That's what you claim, whether you know it or not.

                    So, let me ask you this. Now we take that manometer, and put half of it inside the tank, sealed up so there are no leaks. We fill that manometer with water to the exact level of the water inside.

                    When the 1 PSI of pressure is applied, would the difference in water level in that manometer be DIFFERENT FROM the difference in water level between the original manometer that just is connected to the tank, and the water level in the tank?

                    If so, explain why.

                    If NOT explain why.
                    CNC machines only go through the motions.

                    Ideas expressed may be mine, or from anyone else in the universe.
                    Not responsible for clerical errors. Or those made by lay people either.
                    Number formats and units may be chosen at random depending on what day it is.
                    I reserve the right to use a number system with any integer base without prior notice.
                    Generalizations are understood to be "often" true, but not true in every case.

                    Comment


                    • #40
                      Jerry you are pulling straws out of the haystack, Lets talk real world here, steam pressure gauges are mounted on the top of said boiler. Now if the Homeowner / Expert wants to solve this problem, he needs to go back to the last time it worked correctly and then find out what has changed. All he really needs is perhaps one PSI gauge pressure at the top of the boiler. From my experience working in the real world is more than likely a venting or water issue or at least start there. If might even lead back to the boiler change out.

                      Edit yes he might need more than 1 psig if he has a very tall house, and yes Jerry I worked in the commercial HVAC world for over 30 years, very familiar with all types of gauges. Never saw a manometer used to measure pressure on a steam boiler however.... in the Real world.
                      Last edited by wmgeorge; 01-16-2022, 05:34 PM.
                      Retired - Journeyman Refrigeration Pipefitter - Master Electrician

                      Comment


                      • #41
                        It's not done because it is inconvenient, and breakable, NOT because it does not work. It works fine, although reading a dial is a lot more convenient, and you have to make sure the manometer has water in it (automatic if it connects into the boiler below water level).

                        I'd put a gauge on the top also. My hot water system has a pressure gauge. I like pressure gauges for that sort of application.

                        Point here is not that a manometer is a great practical idea, but it A) works, and needs no "calibration", and B) the OP has one installed which actually should work just fine if it is installed right.

                        If his manometer is installed right, and reads zero PSI, then there is zero PSI in the system.
                        CNC machines only go through the motions.

                        Ideas expressed may be mine, or from anyone else in the universe.
                        Not responsible for clerical errors. Or those made by lay people either.
                        Number formats and units may be chosen at random depending on what day it is.
                        I reserve the right to use a number system with any integer base without prior notice.
                        Generalizations are understood to be "often" true, but not true in every case.

                        Comment


                        • #42
                          If I was on a service call and suspected the gauge not reading correctly I would pull it off and check the calibration or replace the gauge. Instead of mickey mousing around with something else the Homeowner had. When your charging $80 - $120 an hour the customer expects a professional.
                          Retired - Journeyman Refrigeration Pipefitter - Master Electrician

                          Comment


                          • #43
                            Originally posted by wmgeorge View Post
                            If I was on a service call and suspected the gauge not reading correctly I would pull it off and check the calibration or replace the gauge. Instead of mickey mousing around with something else the Homeowner had. When your charging $80 - $120 an hour the customer expects a professional.
                            1st I added a 0-3psi gauge to the 30psi one stock. Nada. Then I flipped open the overpressure release valve. Nothing, no hiss. Then I added the primitive manometer. No pressure. Positively no pressure.

                            It's definitely not about the venting. Venting is like the rudder of the ship, it's useless if there's no way on her, the pressure. I still think the vanishing gas/BTUs is the key.
                            Location: Jersey City NJ USA

                            Comment


                            • #44
                              So how much water is in the boiler, since your the expert? A low pressure steam boiler has no use for a 0-30 psig gauge. BTW when was the last time this system worked normally? Never on a service call rule out anything!!
                              Last edited by wmgeorge; 01-16-2022, 07:45 PM.
                              Retired - Journeyman Refrigeration Pipefitter - Master Electrician

                              Comment


                              • #45
                                Originally posted by wmgeorge View Post
                                So how much water is in the boiler, since your the expert? A low pressure steam boiler has no use for a 0-30 psig gauge. BTW when was the last time this system worked normally?
                                The water is up to the normal level, the autofill is operating according to the tech, and it's not using excess water. All steam boilers are required by law to have a 0-30 psi gauge, an additional lower pressure gauge is optional. The boiler seemed to be working after service last March. I'm still puzzled why the tech didn't analyze combustion when that was the 1st thing he did last year.

                                Click image for larger version  Name:	boiler guage.jpg Views:	0 Size:	53.6 KB ID:	1981150
                                Location: Jersey City NJ USA

                                Comment