I am using a 24v coil contactor to supply power to my 220v AC drives to my axis motors. I was going to run the neutral also through the contactor along with the 220v L1 hot wire. Is that a good or bad idea?
Wiring a contactor for CNC mill?
Originally posted by jmm03 View Posttypically, 220 single phase is 2 line leads and a ground, is german single phase different? (your ground should not be switched, neutral can be) JimLocation: The Black Forest in Germany
By NEC in the US the neutral is bonded with ground at the main service panel. At all other subpanels it is not grounded. At equipment I have seen it both ways, switched and not switched. I have noticed in a switched neutral there doesn't seem to be any wear on the contacts. Under some conditions a neutral can become energized and switching it may be for safety. As far as motor operation, I don't think it makes any difference. Consult your local codes for rules in your area. Is there a German blog where you could do a search on the subject? Trouble with a lot of codes they are not meaningful to the average person. Could be they are trying to protect their source of income or keep ignorant laymen from a dangerous situation.
In most jurisdictions the neutral is not switched, particularly if it is a Earth bonded neutral.
Also generally not necessary, check with the local service company.
I never have in either UK or in N.A.Last edited by MaxHeadRoom; 05-29-2022, 03:23 PM.
In N.A. there is NFPA79 for practices covering Standards for Industrial machinery, and they give examples of Ladder logic control for enclosure wiring which shows the neutral Unbroken throughout.
Also there used to be a practice of placing the contactor O/L on the neutral side of the coil. This is now frowned on and is considered BAD practice.
.Likewise, disconnects and fusing are always in the 'Live' conductors only.
Why is this a question?
Yes, in equipment, the neutral can be opened along with the hot wire. If that is done, the switch will show a different symbol than in cases where it is not done. IIRC, the "O" of the typical "O" and "I" on/off indicator can only be used if the neutral IS opened by the switch. It indicates a complete disconnection.
In the US likewise, some does, some does not.
In fixed wiring, what the NEC refers to as a branch circuit, the neutral should never be opened, as various sorts of hazard can exist if it is opened. That is, for instance, why a corner-grounded branch circuit must have the grounded conductor (neutral) fuse replaced by a solid jumper.
Originally posted by MaxHeadRoom View PostSection 79 of the NFPA79 states that each disconnecting means shall only disconnect all ungrounded conductors of a single supply circuit..
A "disconnecting means" is a switch which is normally not on the machine, but may be on it, and which is intended to render the entire electrical system of the machine inoperative and unpowered, i.e. a "safe" condition in which it can be worked on. It is only necessary in the case of a machine which is hard-wired to the branch circuit, not connected by a plug. (A plug is also recognized as a "disconnecting means", and obviously disconnects all wires including ground).
A power contactor which simply stops and starts the machine is NOT a "disconnecting means", it has a completely different purpose, and the two are not equivalent. That is what the OP is discussing. A power switch would be similar, and also is not a "disconnecting means".
In Europe the only time neutral is grounded is at the power company side or at the main switchboard before the GFCB so, it is not part of the ground protection. This is done by the yellow/green wire that's not connected to the contactor. If you connect the neutral to ground at any part of the circuit, the Ground Fault Circuit Breaker will trip.
On regular domestic/households we are supplied energy by the power company with either a single phase 230V supply and the power limiting circuit breaker from the company is a 2 pole which limits to a maximum of 45A or we can be supplied 3 phase and neutral with a 4 pole circuit breaker with a maximum of 30A per phase. Small businesses can be supplied with a maximum of 60A per phase with a normal low voltage supply. After that, you need a medium voltage transformer, 3 wire, 3 phase input and 4 wire 3 phase plus neutral output. Around towns the medium voltage is 15Kv and in industrial areas, 30Kv. The very high voltage power lines are for long distance runs.Helder Ferreira
Setubal, Portugal
If I get it right it’s just using the contractor terminals as a double pole switch, they are isolated so it wouldn’t matter ( just like the shower pull switch I wired today, and the cooker for that matter, both live L1 and N make or break same time, I read the regs as it’s a requirement in U.K. all your up to is controlling the contacts with the 24v coil.
mark
Short answer, it is probably not necessary but it probably will do no harm.
Do you know if the neutral is even used? If so, describe how.
Originally posted by Black Forest View PostI am using a 24v coil contactor to supply power to my 220v AC drives to my axis motors. I was going to run the neutral also through the contactor along with the 220v L1 hot wire. Is that a good or bad idea?Paul A.
Originally posted by Paul Alciatore View PostShort answer, it is probably not necessary but it probably will do no harm.
Helder Ferreira