    I have a static convertor as well as a rotary and two invertors with speed control.I have learned from here that my static convertor can be used as a rotay convertor with the aid of a motor sat between the outlet of the convertor and the machine I am using.This static convertor is 7.5 hp quite big what size motor should I use for best results, also second part of the question (just to be quite sure as this is potentially dangerous) do you simply as I have implied wire the motor as if your running it for whatever purpose and then take wires from the motor to a box with an outlet for your machine simple as that? Alistair excuse typing
    Please excuse my typing as I have a form of parkinsons disease

  • #2
    You can read installation instructions at http://www.phase-a-matic.com. Information about idler motor wiring is on pdf for each of their static convertors.

    Comment


    • #3
      It is almost that simple, but you DO need to fuse or otherwise protect things, and also make sure that the starting capacitor in the static cannot be re-connected if the voltage sags under load.

      That is all gone through in the Phase-a-Matic literature (about all they are good for IMO).

      However.........

      The static converter is sized for a particular motor. Using it with a smaller HP motor will lead to bad performance, or NO performance.

      It is as bad to over-size a static as it is to under-size.
      1601

      Keep eye on ball.
      Hashim Khan

      Comment


      • #4
        thanks guys so I need as big a motor as the static convertor will take.Alistair