Ok so i get a call to a machine which blows the breaker as soon as the heaters kick in after power-up.
Diagnosis - disconnect one or other of the two SSR's that control the heater bank.
Summary - One SSR is shorted to earth.
Repair - Replace SSR.
Two hours later i get another call, machine is 200c over temperature but controller is showing off on the output.
Summary - SSR shorted internally.
Repair - turn machine off and go for tea break, wait for smoke to clear.
Any ideas on what can kill SSR's like this?
I am guessing the machines were not designed with this fault in mind as there is nothing to kill the power in an overheat situation.
I have only seem them fail short-to-earth before.
???
Diagnosis - disconnect one or other of the two SSR's that control the heater bank.
Summary - One SSR is shorted to earth.
Repair - Replace SSR.
Two hours later i get another call, machine is 200c over temperature but controller is showing off on the output.
Summary - SSR shorted internally.
Repair - turn machine off and go for tea break, wait for smoke to clear.
Any ideas on what can kill SSR's like this?
I am guessing the machines were not designed with this fault in mind as there is nothing to kill the power in an overheat situation.
I have only seem them fail short-to-earth before.
???