Originally posted by flutedchamber
View Post
If you're referring to the Polyspede link in your post, yes, that's a single phase VFD and the recommended breaker is 2X the rated input current. The fuses/breakers are sized to protect the vfd and external wiring in case of an internal vfd failure.
You can't use a 20hp vfd to "replace" a 20hp rpc directly. VFD's drive motors - not machines with transformer, controls etc. For your WEG - forget "HP" and just look at motor current. I'd guess the 10hp single phase vfd will work fine, but you'll need to choose one set of motor windings and use those. Switching pole configuration on the fly for high/low speed is not recommended..
Also.. is your 20hp rpc really a 20hp motor? if it's on a 60amp breaker, probably not. It may be one of these wacky "20hp capable" ratings, with different ratings for single motor startup and total connected load.